E250 temperatures
by Joshua Boyd
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message I just noticed that the thermal error light was lit on my e250 running
solaris 10. A quick login, and prtdiag shows: System Temperatures (Celsius): ------------------------------ CPU0 64 WARNING CPU1 47 MB0 41 MB1 31 PDB 35 SCSI 29 Yet, the fans still aren't full speed: Fan Bank : ---------- Bank Speed Status (0-255) ---- ----- ------ SYS 219 OK What is the real danger region for the E250, and will the light turn off on its own if the temp goes down? Also, does anyone know any tricks to make it balance the thermal load between the two CPUs better? Any other tricks? I would venture to say that the area where the E250 sits is still generally under 70 degrees. The e250 is near the bottom of a short rack that doesn't actually have all that much running in it. Below the e250 is a smartups 1400. The only things running above it are a SS20, a GigE switch, and a FastE switch (the FC array, T1, and Compaq DL360 are off). On top of the rack is a Ultra 5, and a few feet away is an Ultra 80, which doesn't seem to have the same sort of monitoring on it. I may have to get a remote device to monitor the area... Also, does anyone know if 280rs happen to run cooler? _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperaturesReply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Fri, Apr 11, 2008 at 8:18 PM, Joshua Boyd <jdboyd@...> wrote:
> I just noticed that the thermal error light was lit on my e250 running > solaris 10. A quick login, and prtdiag shows: > System Temperatures (Celsius): > ------------------------------ > CPU0 64 WARNING > CPU1 47 > MB0 41 > MB1 31 > PDB 35 > SCSI 29 > > > Yet, the fans still aren't full speed: > Fan Bank : > ---------- > > Bank Speed Status > (0-255) > ---- ----- ------ > SYS 219 OK > > > What is the real danger region for the E250, and will the light turn off > on its own if the temp goes down? > > Also, does anyone know any tricks to make it balance the thermal load > between the two CPUs better? > > Any other tricks? I would venture to say that the area where the E250 > sits is still generally under 70 degrees. The e250 is near the bottom > of a short rack that doesn't actually have all that much running in it. > Below the e250 is a smartups 1400. The only things running above it are > a SS20, a GigE switch, and a FastE switch (the FC array, T1, and Compaq > DL360 are off). On top of the rack is a Ultra 5, and a few feet away is > an Ultra 80, which doesn't seem to have the same sort of monitoring on > it. I may have to get a remote device to monitor the area... > > Also, does anyone know if 280rs happen to run cooler? > _______________________________________________ > rescue list - http://www.sunhelp.org/mailman/listinfo/rescue > Concerning the CPUs: each cpu slot has it own temperature range. The range may be similar or dissimiliar. The temperature range is dependent on the CPU itself, the airflow over the CPU. The closeness of power supplies, hard drives, cards, etc. effect the acceptable temperature of any specific CPU. All this to say, you can't balance the thermal load of a CPU in that vintage Sun server. >From my understanding the UPS unit generate heat that will effect the surrounding equipment. If a device sits on top of the 250 (that is, no air gap), it may cause heating issues. (We once had a shorty rack with a v120 and a 19" switch sitting on top of the server [no air gap but the switch was only half the depth of the v120] and the v120 would crash every few days. We moved the v120 down 1U in the rack and the crashes stopped.] I would suggest that you add fans to the rack if possible and provide air gaps if feasible. _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Joshua Boyd
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Apr 11, 2008, at 9:30 PM, hike wrote:
> > Concerning the CPUs: each cpu slot has it own temperature range. > The range > may be similar or dissimiliar. The temperature range is dependent > on the > CPU itself, the airflow over the CPU. The closeness of power > supplies, hard > drives, cards, etc. effect the acceptable temperature of any > specific CPU. > All this to say, you can't balance the thermal load of a CPU in > that vintage > Sun server. Too bad that they don't have a way to tell it to move work from one CPU to the other until they equalize in this way. >> From my understanding the UPS unit generate heat that will effect the > surrounding equipment. > If a device sits on top of the 250 (that is, no air gap), it may cause > heating issues. (We once had a shorty rack with a v120 and a 19" > switch > sitting on top of the server [no air gap but the switch was only > half the > depth of the v120] and the v120 would crash every few days. We > moved the > v120 down 1U in the rack and the crashes stopped.] > > I would suggest that you add fans to the rack if possible and > provide air > gaps if feasible. Well, I did adjust the rack to allow more space behind the rack (about 24" from the back of the rack to the wall) earlier. And upon your advice, I moved the T1 off the top of the E250 to create a 1U gap between it and the SS20. Although I wouldn't have called the top of the E250 (after I removed the T1) warm to the touch. Tomorrow I will try raising the E250 to have a gap between it and the UPS, if I have time around work. That will require completely tearing the rack apart. I need a larger rack (and perhaps a dedicated air conditioner for the server area). _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Patrick Giagnocavo 717-201-3366
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Joshua Boyd wrote:
> I just noticed that the thermal error light was lit on my e250 running > solaris 10. A quick login, and prtdiag shows: > System Temperatures (Celsius): > ------------------------------ If you can, get either a PCI-powered fan or one that fits in a slot blank but is powered by the 5V molex connector - either kind will exhaust hot air out the back. I am assuming you have already checked for dust, and for perhaps a stray ribbon cable blocking needed airflow. --Patrick _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Joshua Boyd
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Apr 11, 2008, at 10:49 PM, Patrick Giagnocavo wrote:
> Joshua Boyd wrote: >> I just noticed that the thermal error light was lit on my e250 >> running >> solaris 10. A quick login, and prtdiag shows: >> System Temperatures (Celsius): >> ------------------------------ > > If you can, get either a PCI-powered fan or one that fits in a slot > blank but is powered by the 5V molex connector - either kind will > exhaust hot air out the back. I am assuming you have already > checked for dust, and for perhaps a stray ribbon cable blocking > needed airflow. When I move it away from the UPS, I will certainly open it to vacuum out dust. I did vacuum the machine out already this year though. I can look at a PCI fan, but the machine had three big fans across the middle of the case (front to back middle), and a lot of vent holes over top of the PCI slots. _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperaturesReply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Fri, Apr 11, 2008 at 10:18 PM, Joshua Boyd <jdboyd@...> wrote:
> On Apr 11, 2008, at 9:30 PM, hike wrote: > > > > > Concerning the CPUs: each cpu slot has it own temperature range. The > > range > > may be similar or dissimiliar. The temperature range is dependent on > > the > > CPU itself, the airflow over the CPU. The closeness of power supplies, > > hard > > drives, cards, etc. effect the acceptable temperature of any specific > > CPU. > > All this to say, you can't balance the thermal load of a CPU in that > > vintage > > Sun server. > > > > Too bad that they don't have a way to tell it to move work from one CPU to > the other until they equalize in this way. > > From my understanding the UPS unit generate heat that will effect the > > > > > surrounding equipment. > > If a device sits on top of the 250 (that is, no air gap), it may cause > > heating issues. (We once had a shorty rack with a v120 and a 19" switch > > sitting on top of the server [no air gap but the switch was only half > > the > > depth of the v120] and the v120 would crash every few days. We moved > > the > > v120 down 1U in the rack and the crashes stopped.] > > > > I would suggest that you add fans to the rack if possible and provide > > air > > gaps if feasible. > > > > Well, I did adjust the rack to allow more space behind the rack (about 24" > from the back of the rack to the wall) earlier. > > And upon your advice, I moved the T1 off the top of the E250 to create a > 1U gap between it and the SS20. Although I wouldn't have called the top of > the E250 (after I removed the T1) warm to the touch. > > Tomorrow I will try raising the E250 to have a gap between it and the UPS, > if I have time around work. That will require completely tearing the rack > apart. I need a larger rack (and perhaps a dedicated air conditioner for > the server area). > > _______________________________________________ > rescue list - http://www.sunhelp.org/mailman/listinfo/rescue > Too bad that they don't have a way to tell it to move work from one CPU to the other until they equalize in this way. There commands, IIRC, to associate certain processes to specific CPUs. Unfortunately, we never used that outside of class, that is, in the real world. If you have a service contract you Sun support vendor can find out if this is possible. (Maybe the list members know also and will fill-in this [and any other] blank.) _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures & E250 fans
by stephen price
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message we just had to replace 2 of 3 fans in an older e250 in
the data center. both of the failed fans sounded magnificient as screeches & metallic howls reverberated around the otherwise noisy room! keep a close eye for what appears to be at least one imminent fan failure (hope not) in your box. regards steve __________________________________________________ Do You Yahoo!? Tired of spam? Yahoo! Mail has the best spam protection around http://mail.yahoo.com _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Joshua Boyd
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Sat, Apr 12, 2008 at 02:04:18PM -0700, Ron Wickersham wrote:
> so i show a slower fan and lower temperatures. i've been worried that > my room temperature is too high at around 75-degrees F, but have never > gotten a temp warning light in the five years this machine has been running. According to the owners manual, the light comes on if any of the chip sensors hit 60c or if the ambiant sensors hit 53c. Shut down occurs when a chip hits 65c. > i am running both power supplies and 3 disk drives. I am using one PSU and 6 disks. And they aren't particularly cool disks either. Maybe I should try swapping 3 or them for cooler ones. > the two CPUs are the same...are your CPUs different? this machine > is running Solaris 10 with 12 zones and in some of the zones there > are 20 virtual hosts of apache, and some heavy usage in perl scripts > for bulletin board system called Discus, so the perfmeter frequently > shows both CPUs maxed out and the load average up to ten so the > machine isn't just sitting idle. My machine mostly sits idle. It has close to 1.75 gigs of ram. It runs 1 zone. It has dual 300 CPUs instead of dual 400s. > when you have the machine apart, i'd check that all three fans are > putting out the same volume of air, feeling the flow with your hand > should be adequate for that. i could imagine that if one fan were > running slower then the lower airflow could make a difference on the > parts cooled by it. It feels to me like the middle fan puts out more air then the side fans. The middle one goes over the CPUs, one side fan covers the RAM, and the remaining side fan covers the PCI cards (1 GigE card, and 1 dead FC card. I should have removed the FC card, but I didn't think about it until I was connecting it back into the rack. > what kind of computational load are you running? Generally very little. This machine doesn't serve anything publicly. It just serves files (which means it doesn't do much of that when my wife and I aren't home), serves CVS (that I use from work sometimes, but not heavily), and that is it on a day to day basis. >From time to time, I feed it a picture processing load (imagemagick scripts) that max the CPUs and takes hours to run. > >Below the e250 is a smartups 1400. > > is the e250 laying down in the rack-mount orientation or standing up in the > "normal" orientation shown in the product pictures? and assuming that > you have the side panels on the e250 which make the airflow go the way > intended by the design. It is a rack mounted configuration. I would assume I have the proper side panels for rack mounting. > >The only things running above it are > >a SS20, a GigE switch, and a FastE switch (the FC array, T1, and Compaq > >DL360 are off). On top of the rack is a Ultra 5, and a few feet away is > >an Ultra 80, which doesn't seem to have the same sort of monitoring on > >it. I may have to get a remote device to monitor the area... > > in feeling the e250 there is no warmth from anyside of the side panels, > the airflow keeps the case absolutely at room temperature. so i can't > imagine that any gear either above or below would affect its temperature > in any measureable way. It was probably the dust in the fan tray. There was still a lot of airflow, but after cleaning the fans (which I hadn't previously realized were removable), there is still more air moving out the back of the box. At this point, my fan is still running faster than yours, but the CPUs are slightly cooler than yours. prstat shows a load of 0.03 on the machine. _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Ron Wickersham
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Fri, 11 Apr 2008, Joshua Boyd wrote:
> I just noticed that the thermal error light was lit on my e250 running > solaris 10. A quick login, and prtdiag shows: > System Temperatures (Celsius): > ------------------------------ > CPU0 64 WARNING > CPU1 47 > MB0 41 > MB1 31 > PDB 35 > SCSI 29 just checking my system: System Temperatures (Celsius): ------------------------------ CPU0 41 CPU1 44 MB0 34 MB1 29 PDB 28 SCSI 25 > Yet, the fans still aren't full speed: > Fan Bank : > ---------- > > Bank Speed Status > (0-255) > ---- ----- ------ > SYS 219 OK Fan Bank : ---------- Bank Speed Status (0-255) ---- ----- ------ SYS 171 OK so i show a slower fan and lower temperatures. i've been worried that my room temperature is too high at around 75-degrees F, but have never gotten a temp warning light in the five years this machine has been running. this machine is not mounted in a rack, just sitting on the floor, in the stand-up position and has another E250 on the top of it. i am running both power supplies and 3 disk drives. ========================= CPUs ========================= Run Ecache CPU CPU Brd CPU Module MHz MB Impl. Mask --- --- ------- ----- ------ ------ ---- SYS 0 0 400 2.0 US-II 10.0 SYS 1 1 400 2.0 US-II 10.0 ========================= Memory ========================= Interlv. Socket Size Bank Group Name (MB) Status ---- ----- ------ ---- ------ 0 none U0701 128 OK 0 none U0801 128 OK 0 none U0901 128 OK 0 none U1001 128 OK the two CPUs are the same...are your CPUs different? this machine is running Solaris 10 with 12 zones and in some of the zones there are 20 virtual hosts of apache, and some heavy usage in perl scripts for bulletin board system called Discus, so the perfmeter frequently shows both CPUs maxed out and the load average up to ten so the machine isn't just sitting idle. when you have the machine apart, i'd check that all three fans are putting out the same volume of air, feeling the flow with your hand should be adequate for that. i could imagine that if one fan were running slower then the lower airflow could make a difference on the parts cooled by it. > What is the real danger region for the E250, and will the light turn off > on its own if the temp goes down? > > Also, does anyone know any tricks to make it balance the thermal load > between the two CPUs better? what kind of computational load are you running? > Any other tricks? I would venture to say that the area where the E250 > sits is still generally under 70 degrees. this is cooler than the external temperature that my machine is running in. > The e250 is near the bottom > of a short rack that doesn't actually have all that much running in it. that should be the coolest place in the rack > Below the e250 is a smartups 1400. is the e250 laying down in the rack-mount orientation or standing up in the "normal" orientation shown in the product pictures? and assuming that you have the side panels on the e250 which make the airflow go the way intended by the design. > The only things running above it are > a SS20, a GigE switch, and a FastE switch (the FC array, T1, and Compaq > DL360 are off). On top of the rack is a Ultra 5, and a few feet away is > an Ultra 80, which doesn't seem to have the same sort of monitoring on > it. I may have to get a remote device to monitor the area... in feeling the e250 there is no warmth from anyside of the side panels, the airflow keeps the case absolutely at room temperature. so i can't imagine that any gear either above or below would affect its temperature in any measureable way. -ron _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Bill Bradford
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Sat, Apr 12, 2008 at 02:04:18PM -0700, Ron Wickersham wrote:
> just checking my system: If we're going to be posting prtdiag output.. 8-) System Configuration: Sun Microsystems sun4v Sun Fire(TM) T1000 Memory size: 8064 Megabytes ========================= CPUs ================================== CPU CPU Location CPU Freq Implementation Mask ------------ ----- -------- ------------------- ----- MB/CMP0/P0 0 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P1 1 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P2 2 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P3 3 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P4 4 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P5 5 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P6 6 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P7 7 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P8 8 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P9 9 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P10 10 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P11 11 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P12 12 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P13 13 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P14 14 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P15 15 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P16 16 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P17 17 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P18 18 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P19 19 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P20 20 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P21 21 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P22 22 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P23 23 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P24 24 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P25 25 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P26 26 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P27 27 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P28 28 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P29 29 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P30 30 1000 MHz SUNW,UltraSPARC-T1 MB/CMP0/P31 31 1000 MHz SUNW,UltraSPARC-T1 (actually only 8 cores, with 4 threads per core) 8-) I can't wait to make this system the new ohno.mrbill.net. I've had it for a year and a half now, and firmware issues (fixed in development, but not publicly released just yet) have kept me from deploying it. Hopefully in the next month or so. Bill -- Bill Bradford Houston, Texas _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Patrick Giagnocavo 717-201-3366
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Bill Bradford wrote:
> On Sat, Apr 12, 2008 at 02:04:18PM -0700, Ron Wickersham wrote: >> just checking my system: > > If we're going to be posting prtdiag output.. 8-) > > System Configuration: Sun Microsystems sun4v Sun Fire(TM) T1000 > Memory size: 8064 Megabytes > <snipped? > (actually only 8 cores, with 4 threads per core) > > 8-) > Now now, no one likes a show off :-) > I can't wait to make this system the new ohno.mrbill.net. > I've had it for a year and a half now, and firmware issues (fixed > in development, but not publicly released just yet) have > kept me from deploying it. Hopefully in the next month or so. > Are you able to elaborate? How are the other T1 users able to deploy if you cannot? --Patrick _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Carl R. Friend
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Sat, 12 Apr 2008, Bill Bradford wrote:
> If we're going to be posting prtdiag output.. 8-) > > System Configuration: Sun Microsystems sun4v Sun Fire(TM) T1000 > Memory size: 8064 Megabytes > > ========================= CPUs ================================== > > CPU CPU > Location CPU Freq Implementation Mask > ------------ ----- -------- ------------------- ----- > MB/CMP0/P0 0 1000 MHz SUNW,UltraSPARC-T1 > [...] [you bastard] > MB/CMP0/P31 31 1000 MHz SUNW,UltraSPARC-T1 Initially I wanted to post something really full of invective and expletive, but somehow can't. Hell, I can't even post a "prtdiag" output 'cause my front-line SPARC doesn't have it. Some dmesg output will have to do.... SunOS Release 5.5.1 Version Generic_103640-27 [UNIX(R) System V Release 4.0] Copyright (c) 1983-1996, Sun Microsystems, Inc. mem = 98304K (0x6000000) avail mem = 95236096 Ethernet address = 8:0:20:12:de:ee root nexus = SUNW,Sun 4_75 This is, after all, the *rescue* list. Am I the only one who practises what he preaches? ;-) {big ol' wink there!} FWIW, the above is from my SPARCstation 2 that functions as the secondary DNS master for my local domain, as secondary NTP peer (with three other systems) for time synch, and as domain controller for my wife's Windwoes environment. Cheers! +------------------------------------------------+---------------------+ | Carl Richard Friend (UNIX Sysadmin) | West Boylston | | Minicomputer Collector / Enthusiast | Massachusetts, USA | | mailto:crfriend@... +---------------------+ | http://users.rcn.com/crfriend/museum | ICBM: 42:22N 71:47W | +------------------------------------------------+---------------------+ _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Jochen Kunz
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Sat, 12 Apr 2008 19:39:27 -0400 (EDT)
"Carl R. Friend" <crfriend@...> wrote: > FWIW, the above is from my SPARCstation 2 that functions as the > secondary DNS master for my local domain, Primary DNS for unixag-kl.fh-kl.de is a SPARCstation 1 running NetBSD. :-) -- tsch|_, Jochen Homepage: http://www.unixag-kl.fh-kl.de/~jkunz/ _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by der Mouse
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message >> FWIW, the above is from my SPARCstation 2 that functions as the
>> secondary DNS master for my local domain, > Primary DNS for unixag-kl.fh-kl.de is a SPARCstation 1 running > NetBSD. :-) Until fairly recently (months), the primary DNS server for rodents.montreal.qc.ca was a Sun-3/60. (The primary reason for the switch was that I got a UPS and wanted to put the DNS sever on it, and the -3/60 sucks down a lot more power than the DNARD I moved it to.) /~\ The ASCII der Mouse \ / Ribbon Campaign X Against HTML mouse@... / \ Email! 7D C8 61 52 5D E7 2D 39 4E F1 31 3E E8 B3 27 4B _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Joshua Boyd
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Apr 13, 2008, at 1:34 AM, der Mouse wrote:
>>> FWIW, the above is from my SPARCstation 2 that functions as the >>> secondary DNS master for my local domain, >> Primary DNS for unixag-kl.fh-kl.de is a SPARCstation 1 running >> NetBSD. :-) > > Until fairly recently (months), the primary DNS server for > rodents.montreal.qc.ca was a Sun-3/60. (The primary reason for the > switch was that I got a UPS and wanted to put the DNS sever on it, and > the -3/60 sucks down a lot more power than the DNARD I moved it to.) How did you end up with a DNARD? I wish I had a bit more variety in action. Maybe I'll rack mount an EFIKA someday. _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Sridhar Ayengar
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message Joshua Boyd wrote:
> On Apr 13, 2008, at 1:34 AM, der Mouse wrote: > >>>> FWIW, the above is from my SPARCstation 2 that functions as the >>>> secondary DNS master for my local domain, >>> Primary DNS for unixag-kl.fh-kl.de is a SPARCstation 1 running >>> NetBSD. :-) >> >> Until fairly recently (months), the primary DNS server for >> rodents.montreal.qc.ca was a Sun-3/60. (The primary reason for the >> switch was that I got a UPS and wanted to put the DNS sever on it, and >> the -3/60 sucks down a lot more power than the DNARD I moved it to.) > > How did you end up with a DNARD? Indeed. I'd love to have a DNARD. It's too bad they're so hard to find. I'd actually love to have three or four. Peace... Sridhar _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Bill Bradford
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Sat, Apr 12, 2008 at 07:26:04PM -0400, Patrick Giagnocavo wrote:
>> I can't wait to make this system the new ohno.mrbill.net. I've had it for >> a year and a half now, and firmware issues (fixed in development, but >> not publicly released just yet) have kept me from deploying it. >> Hopefully in the next month or so. > > Are you able to elaborate? How are the other T1 users able to deploy if > you cannot? It has to do with the network LOM dropping off the network or suddenly no longer listening to the SSH port. I don't want to deploy the machine if I'm not able to get to a serial console on it for reboots, patching, remote maintenance, etc. The machine is physically in Austin, and I'm 150 miles away in Houston, so it's not like I could just drive over to the datacenter. I've been working with engineers at Sun, and they've identified a bug, done a fix, and it will be in the next revision of firmware for the machine. Bill -- Bill Bradford Houston, Texas _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by Bill Bradford
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Sat, Apr 12, 2008 at 07:39:27PM -0400, Carl R. Friend wrote:
> Initially I wanted to post something really full of invective > and expletive, but somehow can't. Hell, I can't even post a "prtdiag" > output 'cause my front-line SPARC doesn't have it. I thought prtdiag was in Solaris 2.5 - look in /usr/platform/<platform>/sbin/. > This is, after all, the *rescue* list. Am I the only one who > practises what he preaches? ;-) {big ol' wink there!} We still have an Ultra 2 as a DNS/NIS server on one of our subnets. > FWIW, the above is from my SPARCstation 2 that functions as the > secondary DNS master for my local domain, as secondary NTP peer (with > three other systems) for time synch, and as domain controller for my > wife's Windwoes environment. And until a couple of years ago we had a SS2 running 2.6 with 64M RAM as a license server. 8-) They're good machines. Bill -- Bill Bradford Houston, Texas _______________________________________________ rescue list - http://www.sunhelp.org/mailman/listinfo/rescue |
|
|
Re: E250 temperatures
by r.stricklin
::
Rate this Message:
Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message On Apr 13, 2008, at 9:23 AM, Bill Bradford wrote:
> I thought prtdiag was in Solaris 2.5 - look in > /usr/platform/<platform>/sbin/. Not on sun4c. While we're pasting in console excerpts, here's one from my most recent project. IBM AIX PS/2 Operating System - Version 1.3.0 5713-AEQ (C) COPYRIGHT IBM CORP. 1988,1989,1990,1992 LICENSED MATERIAL - PROGRAM PROPERTY OF IBM nudnik login: PS/2 8580-161. Blue Lightning, etc. A more comfortable environment than the AIX 1.2.1 |