I just noticed that the thermal error light was lit on my e250 running
solaris 10.  A quick login, and prtdiag shows:
System Temperatures (Celsius):
------------------------------
      CPU0    64    WARNING
      CPU1    47
       MB0    41
       MB1    31
       PDB    35
      SCSI    29


Yet, the fans still aren't full speed:
Fan Bank :
----------

Bank      Speed     Status
         (0-255)        
----      -----     ------
 SYS       219        OK


What is the real danger region for the E250, and will the light turn off
on its own if the temp goes down?

Also, does anyone know any tricks to make it balance the thermal load
between the two CPUs better?

Any other tricks?  I would venture to say that the area where the E250
sits is still generally under 70 degrees.  The e250 is near the bottom
of a short rack that doesn't actually have all that much running in it.
Below the e250 is a smartups 1400.  The only things running above it are
a SS20, a GigE switch, and a FastE switch (the FC array, T1, and Compaq
DL360 are off).  On top of the rack is a Ultra 5, and a few feet away is
an Ultra 80, which doesn't seem to have the same sort of monitoring on
it.  I may have to get a remote device to monitor the area...

Also, does anyone know if 280rs happen to run cooler?
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by hike :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Fri, Apr 11, 2008 at 8:18 PM, Joshua Boyd <jdboyd@...> wrote:

> I just noticed that the thermal error light was lit on my e250 running
> solaris 10.  A quick login, and prtdiag shows:
> System Temperatures (Celsius):
> ------------------------------
>      CPU0    64    WARNING
>      CPU1    47
>       MB0    41
>       MB1    31
>       PDB    35
>      SCSI    29
>
>
> Yet, the fans still aren't full speed:
> Fan Bank :
> ----------
>
> Bank      Speed     Status
>         (0-255)
> ----      -----     ------
>  SYS       219        OK
>
>
> What is the real danger region for the E250, and will the light turn off
> on its own if the temp goes down?
>
> Also, does anyone know any tricks to make it balance the thermal load
> between the two CPUs better?
>
> Any other tricks?  I would venture to say that the area where the E250
> sits is still generally under 70 degrees.  The e250 is near the bottom
> of a short rack that doesn't actually have all that much running in it.
> Below the e250 is a smartups 1400.  The only things running above it are
> a SS20, a GigE switch, and a FastE switch (the FC array, T1, and Compaq
> DL360 are off).  On top of the rack is a Ultra 5, and a few feet away is
> an Ultra 80, which doesn't seem to have the same sort of monitoring on
> it.  I may have to get a remote device to monitor the area...
>
> Also, does anyone know if 280rs happen to run cooler?
> _______________________________________________
> rescue list - http://www.sunhelp.org/mailman/listinfo/rescue
>


Concerning the CPUs: each cpu slot has it own temperature range.  The range
may be similar or dissimiliar.  The temperature range is dependent on the
CPU itself, the airflow over the CPU.  The closeness of power supplies, hard
drives, cards, etc. effect the acceptable temperature of any specific CPU.
All this to say, you can't balance the thermal load of a CPU in that vintage
Sun server.

>From my understanding the UPS unit generate heat that will effect the
surrounding equipment.
If a device sits on top of the 250 (that is, no air gap), it may cause
heating issues.  (We once had a shorty rack with a v120 and a 19" switch
sitting on top of the server [no air gap but the switch was only half the
depth of the v120] and the v120 would crash every few days.  We moved the
v120 down 1U in the rack and the crashes stopped.]

I would suggest that you add fans to the rack if possible and provide air
gaps if feasible.
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Joshua Boyd :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Apr 11, 2008, at 9:30 PM, hike wrote:

>
> Concerning the CPUs: each cpu slot has it own temperature range.  
> The range
> may be similar or dissimiliar.  The temperature range is dependent  
> on the
> CPU itself, the airflow over the CPU.  The closeness of power  
> supplies, hard
> drives, cards, etc. effect the acceptable temperature of any  
> specific CPU.
> All this to say, you can't balance the thermal load of a CPU in  
> that vintage
> Sun server.

Too bad that they don't have a way to tell it to move work from one  
CPU to the other until they equalize in this way.

>> From my understanding the UPS unit generate heat that will effect the
> surrounding equipment.
> If a device sits on top of the 250 (that is, no air gap), it may cause
> heating issues.  (We once had a shorty rack with a v120 and a 19"  
> switch
> sitting on top of the server [no air gap but the switch was only  
> half the
> depth of the v120] and the v120 would crash every few days.  We  
> moved the
> v120 down 1U in the rack and the crashes stopped.]
>
> I would suggest that you add fans to the rack if possible and  
> provide air
> gaps if feasible.

Well, I did adjust the rack to allow more space behind the rack  
(about 24" from the back of the rack to the wall) earlier.

And upon your advice, I moved the T1 off the top of the E250 to  
create a 1U gap between it and the SS20.  Although I wouldn't have  
called the top of the E250 (after I removed the T1) warm to the touch.

Tomorrow I will try raising the E250 to have a gap between it and the  
UPS, if I have time around work.  That will require completely  
tearing the rack apart.  I need a larger rack (and perhaps a  
dedicated air conditioner for the server area).
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Patrick Giagnocavo 717-201-3366 :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

Joshua Boyd wrote:
> I just noticed that the thermal error light was lit on my e250 running
> solaris 10.  A quick login, and prtdiag shows:
> System Temperatures (Celsius):
> ------------------------------

If you can, get either a PCI-powered fan or one that fits in a slot
blank but is powered by the 5V molex connector - either kind will
exhaust hot air out the back.  I am assuming you have already checked
for dust, and for perhaps a stray ribbon cable blocking needed airflow.

--Patrick
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Joshua Boyd :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Apr 11, 2008, at 10:49 PM, Patrick Giagnocavo wrote:

> Joshua Boyd wrote:
>> I just noticed that the thermal error light was lit on my e250  
>> running
>> solaris 10.  A quick login, and prtdiag shows:
>> System Temperatures (Celsius):
>> ------------------------------
>
> If you can, get either a PCI-powered fan or one that fits in a slot  
> blank but is powered by the 5V molex connector - either kind will  
> exhaust hot air out the back.  I am assuming you have already  
> checked for dust, and for perhaps a stray ribbon cable blocking  
> needed airflow.

When I move it away from the UPS, I will certainly open it to vacuum  
out dust.  I did vacuum the machine out already this year though.

I can look at a PCI fan, but the machine had three big fans across  
the middle of the case (front to back middle), and a lot of vent  
holes over top of the PCI slots.
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by hike :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Fri, Apr 11, 2008 at 10:18 PM, Joshua Boyd <jdboyd@...> wrote:

> On Apr 11, 2008, at 9:30 PM, hike wrote:
>
> >
> > Concerning the CPUs: each cpu slot has it own temperature range.  The
> > range
> > may be similar or dissimiliar.  The temperature range is dependent on
> > the
> > CPU itself, the airflow over the CPU.  The closeness of power supplies,
> > hard
> > drives, cards, etc. effect the acceptable temperature of any specific
> > CPU.
> > All this to say, you can't balance the thermal load of a CPU in that
> > vintage
> > Sun server.
> >
>
> Too bad that they don't have a way to tell it to move work from one CPU to
> the other until they equalize in this way.
>
>  From my understanding the UPS unit generate heat that will effect the
> > >
> > surrounding equipment.
> > If a device sits on top of the 250 (that is, no air gap), it may cause
> > heating issues.  (We once had a shorty rack with a v120 and a 19" switch
> > sitting on top of the server [no air gap but the switch was only half
> > the
> > depth of the v120] and the v120 would crash every few days.  We moved
> > the
> > v120 down 1U in the rack and the crashes stopped.]
> >
> > I would suggest that you add fans to the rack if possible and provide
> > air
> > gaps if feasible.
> >
>
> Well, I did adjust the rack to allow more space behind the rack (about 24"
> from the back of the rack to the wall) earlier.
>
> And upon your advice, I moved the T1 off the top of the E250 to create a
> 1U gap between it and the SS20.  Although I wouldn't have called the top of
> the E250 (after I removed the T1) warm to the touch.
>
> Tomorrow I will try raising the E250 to have a gap between it and the UPS,
> if I have time around work.  That will require completely tearing the rack
> apart.  I need a larger rack (and perhaps a dedicated air conditioner for
> the server area).
>
> _______________________________________________
> rescue list - http://www.sunhelp.org/mailman/listinfo/rescue
>


Too bad that they don't have a way to tell it to move work from one CPU to
the other until they equalize in this way.


There commands, IIRC, to associate certain processes to specific CPUs.
Unfortunately, we never used that outside of class, that is, in the real
world.

If you have a service contract you Sun support vendor can find out if this
is possible.  (Maybe the list members know also and will fill-in this [and
any other] blank.)
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures & E250 fans

by stephen price :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

we just had to replace 2 of 3 fans in an older e250 in
the data center.

both of the failed fans sounded magnificient as
screeches & metallic howls reverberated around the
otherwise noisy room!

keep a close eye for what appears to be at least one
imminent fan failure (hope not) in your box.

regards
steve


__________________________________________________
Do You Yahoo!?
Tired of spam?  Yahoo! Mail has the best spam protection around
http://mail.yahoo.com 
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Joshua Boyd :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Sat, Apr 12, 2008 at 02:04:18PM -0700, Ron Wickersham wrote:

> so i show a slower fan and lower temperatures.   i've been worried that
> my room temperature is too high at around 75-degrees F, but have never
> gotten a temp warning light in the five years this machine has been running.

According to the owners manual, the light comes on if any of the chip
sensors hit 60c or if the ambiant sensors hit 53c.  Shut down occurs
when a chip hits 65c.
 
> i am running both power supplies and 3 disk drives.

I am using one PSU and 6 disks.  And they aren't particularly cool disks
either.  

Maybe I should try swapping 3 or them for cooler ones.

> the two CPUs are the same...are your CPUs different?   this machine
> is running Solaris 10 with 12 zones and in some of the zones there
> are 20 virtual hosts of apache, and some heavy usage in perl scripts
> for bulletin board system called Discus, so the perfmeter frequently
> shows both CPUs maxed out and the load average up to ten so the
> machine isn't just sitting idle.

My machine mostly sits idle.  It has close to 1.75 gigs of ram.  It runs
1 zone.  It has dual 300 CPUs instead of dual 400s.
 
> when you have the machine apart, i'd check that all three fans are
> putting out the same volume of air, feeling the flow with your hand
> should be adequate for that.  i could imagine that if one fan were
> running slower then the lower airflow could make a difference on the
> parts cooled by it.

It feels to me like the middle fan puts out more air then the side
fans.  The middle one goes over the CPUs, one side fan covers the RAM,
and the remaining side fan covers the PCI cards (1 GigE card, and 1 dead
FC card.  I should have removed the FC card, but I didn't think about it
until I was connecting it back into the rack.
 
> what kind of computational load are you running?

Generally very little.  This machine doesn't serve anything publicly.
It just serves files (which means it doesn't do much of that when my
wife and I aren't home), serves CVS (that I use from work sometimes, but
not heavily), and that is it on a day to day basis.

>From time to time, I feed it a picture processing load (imagemagick
scripts) that max the CPUs and takes hours to run.
 
> >Below the e250 is a smartups 1400.
>
> is the e250 laying down in the rack-mount orientation or standing up in the
> "normal" orientation shown in the product pictures?   and assuming that
> you have the side panels on the e250 which make the airflow go the way
> intended by the design.

It is a rack mounted configuration.  I would assume I have the proper
side panels for rack mounting.
 

> >The only things running above it are
> >a SS20, a GigE switch, and a FastE switch (the FC array, T1, and Compaq
> >DL360 are off).  On top of the rack is a Ultra 5, and a few feet away is
> >an Ultra 80, which doesn't seem to have the same sort of monitoring on
> >it.  I may have to get a remote device to monitor the area...
>
> in feeling the e250 there is no warmth from anyside of the side panels,
> the airflow keeps the case absolutely at room temperature.   so i can't
> imagine that any gear either above or below would affect its temperature
> in any measureable way.


It was probably the dust in the fan tray.  There was still a lot of
airflow, but after cleaning the fans (which I hadn't previously realized
were removable), there is still more air moving out the back of the box.

At this point, my fan is still running faster than yours, but the CPUs
are slightly cooler than yours.  prstat shows a load of 0.03 on the
machine.    
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Ron Wickersham :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Fri, 11 Apr 2008, Joshua Boyd wrote:

> I just noticed that the thermal error light was lit on my e250 running
> solaris 10.  A quick login, and prtdiag shows:
> System Temperatures (Celsius):
> ------------------------------
>      CPU0    64    WARNING
>      CPU1    47
>       MB0    41
>       MB1    31
>       PDB    35
>      SCSI    29

just checking my system:

System Temperatures (Celsius):
------------------------------
       CPU0    41
       CPU1    44
        MB0    34
        MB1    29
        PDB    28
       SCSI    25

> Yet, the fans still aren't full speed:
> Fan Bank :
> ----------
>
> Bank      Speed     Status
>         (0-255)
> ----      -----     ------
> SYS       219        OK

Fan Bank :
----------

Bank      Speed     Status
          (0-255)
----      -----     ------
  SYS       171        OK

so i show a slower fan and lower temperatures.   i've been worried that
my room temperature is too high at around 75-degrees F, but have never
gotten a temp warning light in the five years this machine has been running.

this machine is not mounted in a rack, just sitting on the floor, in the
stand-up position and has another E250 on the top of it.

i am running both power supplies and 3 disk drives.

========================= CPUs =========================

                     Run   Ecache   CPU    CPU
Brd  CPU   Module   MHz     MB    Impl.   Mask
---  ---  -------  -----  ------  ------  ----
SYS     0     0      400     2.0   US-II    10.0
SYS     1     1      400     2.0   US-II    10.0


========================= Memory =========================

        Interlv.  Socket   Size
Bank    Group     Name    (MB)  Status
----    -----    ------   ----  ------
   0      none     U0701   128      OK
   0      none     U0801   128      OK
   0      none     U0901   128      OK
   0      none     U1001   128      OK

the two CPUs are the same...are your CPUs different?   this machine
is running Solaris 10 with 12 zones and in some of the zones there
are 20 virtual hosts of apache, and some heavy usage in perl scripts
for bulletin board system called Discus, so the perfmeter frequently
shows both CPUs maxed out and the load average up to ten so the
machine isn't just sitting idle.

when you have the machine apart, i'd check that all three fans are
putting out the same volume of air, feeling the flow with your hand
should be adequate for that.  i could imagine that if one fan were
running slower then the lower airflow could make a difference on the
parts cooled by it.

> What is the real danger region for the E250, and will the light turn off
> on its own if the temp goes down?
>
> Also, does anyone know any tricks to make it balance the thermal load
> between the two CPUs better?

what kind of computational load are you running?

> Any other tricks?  I would venture to say that the area where the E250
> sits is still generally under 70 degrees.

this is cooler than the external temperature that my machine is running
in.

> The e250 is near the bottom
> of a short rack that doesn't actually have all that much running in it.

that should be the coolest place in the rack

> Below the e250 is a smartups 1400.

is the e250 laying down in the rack-mount orientation or standing up in the
"normal" orientation shown in the product pictures?   and assuming that
you have the side panels on the e250 which make the airflow go the way
intended by the design.

> The only things running above it are
> a SS20, a GigE switch, and a FastE switch (the FC array, T1, and Compaq
> DL360 are off).  On top of the rack is a Ultra 5, and a few feet away is
> an Ultra 80, which doesn't seem to have the same sort of monitoring on
> it.  I may have to get a remote device to monitor the area...

in feeling the e250 there is no warmth from anyside of the side panels,
the airflow keeps the case absolutely at room temperature.   so i can't
imagine that any gear either above or below would affect its temperature
in any measureable way.

-ron
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Bill Bradford :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Sat, Apr 12, 2008 at 02:04:18PM -0700, Ron Wickersham wrote:
> just checking my system:

If we're going to be posting prtdiag output.. 8-)

System Configuration:  Sun Microsystems  sun4v Sun Fire(TM) T1000
Memory size: 8064 Megabytes

========================= CPUs ==================================

                            CPU                 CPU  
Location     CPU   Freq     Implementation      Mask
------------ ----- -------- ------------------- -----
MB/CMP0/P0       0 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P1       1 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P2       2 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P3       3 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P4       4 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P5       5 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P6       6 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P7       7 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P8       8 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P9       9 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P10     10 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P11     11 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P12     12 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P13     13 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P14     14 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P15     15 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P16     16 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P17     17 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P18     18 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P19     19 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P20     20 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P21     21 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P22     22 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P23     23 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P24     24 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P25     25 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P26     26 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P27     27 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P28     28 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P29     29 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P30     30 1000 MHz  SUNW,UltraSPARC-T1        
MB/CMP0/P31     31 1000 MHz  SUNW,UltraSPARC-T1        

(actually only 8 cores, with 4 threads per core)

8-)

I can't wait to make this system the new ohno.mrbill.net.
I've had it for a year and a half now, and firmware issues (fixed
in development, but not publicly released just yet) have
kept me from deploying it.  Hopefully in the next month or so.

Bill

--
Bill Bradford
Houston, Texas
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Patrick Giagnocavo 717-201-3366 :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

Bill Bradford wrote:

> On Sat, Apr 12, 2008 at 02:04:18PM -0700, Ron Wickersham wrote:
>> just checking my system:
>
> If we're going to be posting prtdiag output.. 8-)
>
> System Configuration:  Sun Microsystems  sun4v Sun Fire(TM) T1000
> Memory size: 8064 Megabytes
> <snipped?
> (actually only 8 cores, with 4 threads per core)
>
> 8-)
>

Now now, no one likes a show off :-)

> I can't wait to make this system the new ohno.mrbill.net.
> I've had it for a year and a half now, and firmware issues (fixed
> in development, but not publicly released just yet) have
> kept me from deploying it.  Hopefully in the next month or so.
>

Are you able to elaborate?  How are the other T1 users able to deploy if
you cannot?

--Patrick
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Carl R. Friend :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

    On Sat, 12 Apr 2008, Bill Bradford wrote:

> If we're going to be posting prtdiag output.. 8-)
>
> System Configuration:  Sun Microsystems  sun4v Sun Fire(TM) T1000
> Memory size: 8064 Megabytes
>
> ========================= CPUs ==================================
>
>                            CPU                 CPU
> Location     CPU   Freq     Implementation      Mask
> ------------ ----- -------- ------------------- -----
> MB/CMP0/P0       0 1000 MHz  SUNW,UltraSPARC-T1
> [...] [you bastard]
> MB/CMP0/P31     31 1000 MHz  SUNW,UltraSPARC-T1

    Initially I wanted to post something really full of invective
and expletive, but somehow can't.  Hell, I can't even post a "prtdiag"
output 'cause my front-line SPARC doesn't have it.  Some dmesg output
will have to do....

SunOS Release 5.5.1 Version Generic_103640-27 [UNIX(R) System V Release
4.0]
Copyright (c) 1983-1996, Sun Microsystems, Inc.
mem = 98304K (0x6000000)
avail mem = 95236096
Ethernet address = 8:0:20:12:de:ee
root nexus = SUNW,Sun 4_75

    This is, after all, the *rescue* list.  Am I the only one who
practises what he preaches?  ;-)  {big ol' wink there!}

    FWIW, the above is from my SPARCstation 2 that functions as the
secondary DNS master for my local domain, as secondary NTP peer (with
three other systems) for time synch, and as domain controller for my
wife's Windwoes environment.

    Cheers!

+------------------------------------------------+---------------------+
| Carl Richard Friend (UNIX Sysadmin)            | West Boylston       |
| Minicomputer Collector / Enthusiast            | Massachusetts, USA  |
| mailto:crfriend@...                        +---------------------+
| http://users.rcn.com/crfriend/museum           | ICBM: 42:22N 71:47W |
+------------------------------------------------+---------------------+
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Jochen Kunz :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Sat, 12 Apr 2008 19:39:27 -0400 (EDT)
"Carl R. Friend" <crfriend@...> wrote:

>     FWIW, the above is from my SPARCstation 2 that functions as the
> secondary DNS master for my local domain,
Primary DNS for unixag-kl.fh-kl.de is a SPARCstation 1 running NetBSD.
:-)
--


tsch|_,
       Jochen

Homepage: http://www.unixag-kl.fh-kl.de/~jkunz/
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by der Mouse :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

>> FWIW, the above is from my SPARCstation 2 that functions as the
>> secondary DNS master for my local domain,
> Primary DNS for unixag-kl.fh-kl.de is a SPARCstation 1 running
> NetBSD.  :-)

Until fairly recently (months), the primary DNS server for
rodents.montreal.qc.ca was a Sun-3/60.  (The primary reason for the
switch was that I got a UPS and wanted to put the DNS sever on it, and
the -3/60 sucks down a lot more power than the DNARD I moved it to.)

/~\ The ASCII der Mouse
\ / Ribbon Campaign
 X  Against HTML       mouse@...
/ \ Email!     7D C8 61 52 5D E7 2D 39  4E F1 31 3E E8 B3 27 4B
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Joshua Boyd :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Apr 13, 2008, at 1:34 AM, der Mouse wrote:

>>> FWIW, the above is from my SPARCstation 2 that functions as the
>>> secondary DNS master for my local domain,
>> Primary DNS for unixag-kl.fh-kl.de is a SPARCstation 1 running
>> NetBSD.  :-)
>
> Until fairly recently (months), the primary DNS server for
> rodents.montreal.qc.ca was a Sun-3/60.  (The primary reason for the
> switch was that I got a UPS and wanted to put the DNS sever on it, and
> the -3/60 sucks down a lot more power than the DNARD I moved it to.)

How did you end up with a DNARD?

I wish I had a bit more variety in action.  Maybe I'll rack mount an  
EFIKA someday.
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Sridhar Ayengar :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

Joshua Boyd wrote:

> On Apr 13, 2008, at 1:34 AM, der Mouse wrote:
>
>>>> FWIW, the above is from my SPARCstation 2 that functions as the
>>>> secondary DNS master for my local domain,
>>> Primary DNS for unixag-kl.fh-kl.de is a SPARCstation 1 running
>>> NetBSD.  :-)
>>
>> Until fairly recently (months), the primary DNS server for
>> rodents.montreal.qc.ca was a Sun-3/60.  (The primary reason for the
>> switch was that I got a UPS and wanted to put the DNS sever on it, and
>> the -3/60 sucks down a lot more power than the DNARD I moved it to.)
>
> How did you end up with a DNARD?

Indeed.  I'd love to have a DNARD.  It's too bad they're so hard to
find.  I'd actually love to have three or four.

Peace...  Sridhar
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Bill Bradford :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Sat, Apr 12, 2008 at 07:26:04PM -0400, Patrick Giagnocavo wrote:
>> I can't wait to make this system the new ohno.mrbill.net. I've had it for
>> a year and a half now, and firmware issues (fixed in development, but
>> not publicly released just yet) have kept me from deploying it.
>> Hopefully in the next month or so.
>
> Are you able to elaborate?  How are the other T1 users able to deploy if
> you cannot?

It has to do with the network LOM dropping off the network or suddenly
no longer listening to the SSH port.  I don't want to deploy the machine
if I'm not able to get to a serial console on it for reboots, patching,
remote maintenance, etc.

The machine is physically in Austin, and I'm 150 miles away in Houston,
so it's not like I could just drive over to the datacenter.

I've been working with engineers at Sun, and they've identified a bug,
done a fix, and it will be in the next revision of firmware for the
machine.

Bill

--
Bill Bradford
Houston, Texas
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by Bill Bradford :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Sat, Apr 12, 2008 at 07:39:27PM -0400, Carl R. Friend wrote:
>    Initially I wanted to post something really full of invective
> and expletive, but somehow can't.  Hell, I can't even post a "prtdiag"
> output 'cause my front-line SPARC doesn't have it.  

I thought prtdiag was in Solaris 2.5 - look in
/usr/platform/<platform>/sbin/.

>    This is, after all, the *rescue* list.  Am I the only one who
> practises what he preaches?  ;-)  {big ol' wink there!}

We still have an Ultra 2 as a DNS/NIS server on one of our subnets.

>    FWIW, the above is from my SPARCstation 2 that functions as the
> secondary DNS master for my local domain, as secondary NTP peer (with
> three other systems) for time synch, and as domain controller for my
> wife's Windwoes environment.

And until a couple of years ago we had a SS2 running 2.6 with 64M RAM
as a license server. 8-)  They're good machines.

Bill

--
Bill Bradford
Houston, Texas
_______________________________________________
rescue list - http://www.sunhelp.org/mailman/listinfo/rescue

Re: E250 temperatures

by r.stricklin :: Rate this Message:

Reply (Restricted by the Administrator) | Reply to Author | View Threaded | Show Only this Message

On Apr 13, 2008, at 9:23 AM, Bill Bradford wrote:

> I thought prtdiag was in Solaris 2.5 - look in
> /usr/platform/<platform>/sbin/.

Not on sun4c.

While we're pasting in console excerpts, here's one from my most  
recent project.


IBM AIX PS/2 Operating System - Version 1.3.0
5713-AEQ (C) COPYRIGHT IBM CORP. 1988,1989,1990,1992
LICENSED MATERIAL - PROGRAM PROPERTY OF IBM
nudnik
login:

PS/2 8580-161. Blue Lightning, etc. A more comfortable environment  
than the AIX 1.2.1